I am getting a maximum trip time of 2 seconds. The protective device arcing fault current is 4kA.
As I have put only relay in the upstream and no breaker is there. Can I safely assume that the upstream device will trip prior to 2 sec as the protective device arcing fault current is around 4kA? I have my instantaneous setting of relay at 5.8kA.