vreijb
Electrical
- Nov 22, 2006
- 38
I am performing Arc Flash for a plant with many small 15,25,27.5,50KVA center tapped transformers feeding LV Panelboards. The result from the Arc Flash Calculations are very High and probably not practical.
Is there assumptions made in this situations similar to LV 3-Phase system Like for V<240V and Ib<2K, IE=1,2cal/cm.sq.
The fault currents on single phase are usually lower, and weather the arc will be sustainable at low KA and Volatge
Any comments on interpretation of IEEE 1584-2018 related to above is appreciated
Is there assumptions made in this situations similar to LV 3-Phase system Like for V<240V and Ib<2K, IE=1,2cal/cm.sq.
The fault currents on single phase are usually lower, and weather the arc will be sustainable at low KA and Volatge
Any comments on interpretation of IEEE 1584-2018 related to above is appreciated