- Aug 7, 2001
- 110
I am working with a Client who has given me a reference to a table from NFPA 70E Table 130.7(C) (15) (a).
The line item from that table states that the task when opening hinged covers (to expose bare, energized electrical conductors and circuit parts) in Metal Clad Switchgear, 1kV through 38kV maximum of 35kA (12 cylcle clearing) minimum of 36 in working clearance results in a category 3 risk. Our equipment is a SQ D MasterClad 5kV SWGR main breaker compartment. I would also offer that the SQ D rep states that when the 5kV breaker is racked in that the bus or stabs are not exposed inside the cell.
A senior Power system Analysis engineer stated that once an Arc Flash Calculation has been performed that the Calculation method supersedes any table method. The Calculation method put the equipment in a Category 4 risk.
The task is to simply open the door and inspect a power meter for a Ethernet or Modbus connection. Is using the table method for opening the door just to inspect a legitimate procedure, or are we bound to the Label that the equipment is listed as based on the Arc Flash Calculation method.
Please in your responses list the code reference that defends your answer. I have read briefly through NFPA 70E and can not find this reference that my senior engineer spoke of. He said that the reference is somewhat vague but exists.
Thanks in advance,
JBUDA54
The line item from that table states that the task when opening hinged covers (to expose bare, energized electrical conductors and circuit parts) in Metal Clad Switchgear, 1kV through 38kV maximum of 35kA (12 cylcle clearing) minimum of 36 in working clearance results in a category 3 risk. Our equipment is a SQ D MasterClad 5kV SWGR main breaker compartment. I would also offer that the SQ D rep states that when the 5kV breaker is racked in that the bus or stabs are not exposed inside the cell.
A senior Power system Analysis engineer stated that once an Arc Flash Calculation has been performed that the Calculation method supersedes any table method. The Calculation method put the equipment in a Category 4 risk.
The task is to simply open the door and inspect a power meter for a Ethernet or Modbus connection. Is using the table method for opening the door just to inspect a legitimate procedure, or are we bound to the Label that the equipment is listed as based on the Arc Flash Calculation method.
Please in your responses list the code reference that defends your answer. I have read briefly through NFPA 70E and can not find this reference that my senior engineer spoke of. He said that the reference is somewhat vague but exists.
Thanks in advance,
JBUDA54