WDeanN
Electrical
- Jul 12, 2007
- 38
Here at our facility we have several large synchronous motors. The question of motor contribution to our arc flash hazard has recently come up, especially with a software upgrade to SKM Power Tools for Windows, version 6.0.2.1, which allows the user to specify synchronous motor contributions over a time period. On one bus in particular, because there was no protective device on the motor that would clear the fault quickly, (we are using a two second maximum for our calculations, unless other conditions warrant otherwise) the motor contribution to the arc flash hazard was very significant. The calculations revealed 17 cal/cm2 with all 6 synchronous machines running, but only 2 cal/cm2 with no motors running.
While trying to research our options, I came across an article by J. C. Das, "Design Aspects of Industrial Distribution Systems to Limit Arc Flash Hazard" in the Nov/Dec 2005 issue of IEEE Transactions on Industry Applications. Mr. Das states that "The synchronous motor short-circuit contribution can be neglected in six to eight cycles."
Although he doesn't reference it directly, I found support for this in the 1997 edition of IEEE 399, the IEEE Brown Book. Chapter seven addresses short circuit studies.
Section 7.4.1 states:
Time delayed currents are the short-circuit currents that exist beyond 6 cycles (and up to 30 cycles) from the fault initiation. They are useful in determining currents sensed by time delayed relays and in assessing the sensitivity of overcurrent relays. These currents are assumed to contain no dc offset. Induction and synchronous motor contributions are neglected, and the contributing generators are assumed to have attained transient or higher value reactances (see Table 7-1).
This can also be found in the 1993 edition of IEEE 141, the IEEE Red Book. Chapter four addresses short circuit studies. Section 4.5.4.3 states:
For an application of time delay relays beyond six cycles, the equivalent system network representation will include only generators and passive elements, such as transformers and cables between the generators and the point of short circuit. The generators are represented by transient impedance or a larger impedance related to the magnitude of decaying generator short-circuit current at the specified calculation time. All motor contributions are omitted.
This is for breaker duty calculations, so the question remains: Can this be applied to arc flash studies? Otherwise, what is a reasonable time to assume for the motor contribution to an arc flash event at the upstream bus?
While trying to research our options, I came across an article by J. C. Das, "Design Aspects of Industrial Distribution Systems to Limit Arc Flash Hazard" in the Nov/Dec 2005 issue of IEEE Transactions on Industry Applications. Mr. Das states that "The synchronous motor short-circuit contribution can be neglected in six to eight cycles."
Although he doesn't reference it directly, I found support for this in the 1997 edition of IEEE 399, the IEEE Brown Book. Chapter seven addresses short circuit studies.
Section 7.4.1 states:
Time delayed currents are the short-circuit currents that exist beyond 6 cycles (and up to 30 cycles) from the fault initiation. They are useful in determining currents sensed by time delayed relays and in assessing the sensitivity of overcurrent relays. These currents are assumed to contain no dc offset. Induction and synchronous motor contributions are neglected, and the contributing generators are assumed to have attained transient or higher value reactances (see Table 7-1).
This can also be found in the 1993 edition of IEEE 141, the IEEE Red Book. Chapter four addresses short circuit studies. Section 4.5.4.3 states:
For an application of time delay relays beyond six cycles, the equivalent system network representation will include only generators and passive elements, such as transformers and cables between the generators and the point of short circuit. The generators are represented by transient impedance or a larger impedance related to the magnitude of decaying generator short-circuit current at the specified calculation time. All motor contributions are omitted.
This is for breaker duty calculations, so the question remains: Can this be applied to arc flash studies? Otherwise, what is a reasonable time to assume for the motor contribution to an arc flash event at the upstream bus?