Callumrb30
Electrical
- Oct 12, 2020
- 2
Good Morning/Afternoon,
I am new to the forum and not 100% sure on etiquette for these kinds of queries, so I will keep it brief.
I am in the process of performing an arc flash study (using ETAP), and I have got an unusual looking switching room that I need to model (see attached image).
In the picture, you should be able to see LV circuit breakers mounted on a backboard, with no enclosures. Further to this, several of the CBs have exposed terminals/conductors, which can be seen rising from the top of the breaker and bending backwards behind the panel.
The question I have is - what is the most suitable electrode configuration to use from IEEE 1584? Clearly the breakers are not in enclosures, however the electrodes are not in open air, at least not fully.
Thanks for your time.
Kind regards,
Callum
I am new to the forum and not 100% sure on etiquette for these kinds of queries, so I will keep it brief.
I am in the process of performing an arc flash study (using ETAP), and I have got an unusual looking switching room that I need to model (see attached image).
In the picture, you should be able to see LV circuit breakers mounted on a backboard, with no enclosures. Further to this, several of the CBs have exposed terminals/conductors, which can be seen rising from the top of the breaker and bending backwards behind the panel.
The question I have is - what is the most suitable electrode configuration to use from IEEE 1584? Clearly the breakers are not in enclosures, however the electrodes are not in open air, at least not fully.
Thanks for your time.
Kind regards,
Callum