Dumbo2929
Electrical
- May 31, 2005
- 109
I have a strange question for those familiar with IEEE 1584 and NFPA 70E. A big boss at a big A&E company recently made the following statement. He said that he recommends neutral reactors on service entrance transformers (480Y/277V) because it will limit the arc flash exposure.
It is true that the netral reactor will limit line-to-ground fault current, but how does this lower the arc flash hazard, when the three-phase bolted fault produces the worstcase fault current and highest incident energy.
Does anyone have any thoughts on this? I rarely see neutral reactors on commercial service entrance transformers, and if this statement was true, I would suspect to see a lot more.
It is true that the netral reactor will limit line-to-ground fault current, but how does this lower the arc flash hazard, when the three-phase bolted fault produces the worstcase fault current and highest incident energy.
Does anyone have any thoughts on this? I rarely see neutral reactors on commercial service entrance transformers, and if this statement was true, I would suspect to see a lot more.