prc
Electrical
- Aug 18, 2001
- 2,013
When large transformers are energised a momentary arcing flash can be noticed across the tank flange (curb) joints at one or two locations.Normally cover and tank are bonded by earthing strips at two locations,but still the arc can be noticed.The earthing through the connecting bolts will not be effective due to paint film etc. The reason for this arcing seems the sudden charging of the ground capacitance between the winding to earthed tank brings up tank potential momentarily causing an arc to cover which will be at less potential.Any contributions?