Are conduit or pipe threads used in Class 1, Div 1 Enviroments? 2

Status
Not open for further replies.

chinalake

Electrical
Aug 14, 2002
1
I am not clear on which type of dies to use threading 1/2" conduit for a Class 1, Div 1 installation. My understanding is that conduit threads are "straight threads" for mechanical construction, and that pipe threads are tapered for sealing. The NEC 346-8 refers to ANSI B.1.20.1. Is there something I missed in the NEC or ANSI B.1.20.1 that states which treads should be used?
 
Replies continue below

Recommended for you

All conduit threads are required to be tapered threads. Conduit couplings use straight threads, but the conduit itself uses the same threads as plumbing pipe. 344.28 (348-8 in the '99 code)in the NEC requires all field cut conduit threads to have a 3/4" to the foot taper.

Don
 
Other supporting verbiage:

99NEC500-3. General.
(d) Threaded Conduit. All threaded conduit referred to herein shall be threaded with an NPT standard conduit cutting die that provides 3⁄4-in. taper per foot. Such conduit shall be made wrenchtight to prevent sparking when fault current flows through the conduit system, and ensure the explosionproof or dust-ignitionproof integrity of the conduit system where applicable.

 
A field note...
If you are preparing a spec for conduit, please do add that an anti-seize compound be applied to all threads prior to final assembly.
cheers.
a.
 
Good point, Abeltio. The 2002 code requires an approved conductive corrosion protective coating for all field cut threads in area where the conduit requires corrosion protection. See 300.6(A).
Don
 
You said that "344.28 (348-8 in the '99 code)in the NEC requires all field cut conduit threads to have a 3/4" to the foot taper." Does this also apply to factory threaded conduit?



 
Column 1 calls out the ¾-inch-per-foot taper and ANSI B.1.20.1. It’s very likely that listed galvanized-steel and aluminum conduit and IMC have the same characteristics. The details would probably be described in the corresponding UL standard.
 