All UL listed Explosion Proof Motors have factory seals for the wires leaving the motor housing and entering the motor conduit box.
For a Class I, Div 1, Group D enviroment installation a UL listed motor for the area, is it necessary to also install conduit seals (ie Crouse Hinds EYS fittings) at the motor conduit box?
I believe it is not necessary because inside the box is only wire splices, not arcing contacts or hot components.
However, NEC 501.15(A)(1)(2) says seals are required for trade size 2" or larger and the enclosure contains terminals, splices, or taps.
Are you putting seals on all EX motor conduit boxes, only those 2" or larger, or never on any regardless of size.