Are automatic tap changers still recommended for a 10 or 12% impedance, 132 or 66 to 22kv distribution transformer where source voltage does not deviate beyond 1.00pu?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
tinfoil said:1) Have you done the math on the delivered secondary voltage delivered when the load can vary from 10 to 105%? A 12% xmfr will see 'regulation' across this range, even if the source was really 1.00 p.u. all the time. (BTW, although the relationship is not quite linear, higher %Z implies greater internal voltage regulation with varying load)
tinfoil said:2) Have you added in the +- 1.5% source variation you mentioned to the worst case of (1)?
tinfoil said:3) Is there ANY possibility of a variance from this source of more than 1.5% under THEIR emergency conditions? What is their ALLOWABLE range rather than the range you usually see? Did you allow for this in your answer to (1)?
tinfoil said:4) Is there a GUARANTEE that the supplier's regulators will always be present and functional, or is that simply an artifact of their present configuration?
tinfoil said:5) Is there any possibility that you could be supplied from a more distant source under planned maintenance or emergency contingency plans? Have you allowed for the worst case from that?
tinfoil said:6) Is there any chance that you may want to move these units somewhere else in your system where a tap-changer would be needed?
tinfoil said:7) Does your organization have to match specs on their xmfrs for 'spares' purposes? Do these other xmfrs have tap-changers?
tinfoil said:If you are satisfied with the answer to all of these and still do not see a need for tap-changers, than maybe you can do without.