bdn2004
Electrical
- Jan 27, 2007
- 799
We've got a line-up of forklift battery chargers fed from a 600A, 480V panelboard. The total connected load on the panel is 608 amps. The Plant wants to install some garage door openers on the spare breakers in that panel. Without connecting power monitors and recorders is there a scientific answer to that could justify the additional load? Like a typical demand factor for multiple battery chargers in an industrial facility?