Area of coverage from overhead shield wires in a substation

Status
Not open for further replies.

livewire9

Structural
Aug 4, 2010
49
Typically, shield (static) wires are considered to provide a 30 degree cone of protection on either side of the wire. Can this value be increased for shield wires running side-by-side, at the same height above grade?
 
Replies continue below

Recommended for you

EVERY POINT of a well-bonded/grounded shield wire provides a cone of protection.

For a linear shield wire, this volume looks more like a triangular prism in the middle area.

Having two or more shield wires can give you overlapping coverages.

Just remember that you need to shield your equipment (and personnel) at the elevation of their tops, not just at grade.

This diagram should make it clear:
zone-protection.jpg
 