SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,244
I have a Light Hazard building with a ceiling exactly 20'-0" AFF so I can apply the ceiling height reduction using quick response sprinklers except we do have skylights.
The top of the skylights are at 24'-0" AFF so the upright QR sprinkler protecting the skylight is around 23'-0".
Can I apply the area reduction based on 20'-0" ceiling height? I think I can but I've never had this come up before.
Let me add just to make sure I am on the safe side I'll go with without the area reduction because I like to play safe.
The top of the skylights are at 24'-0" AFF so the upright QR sprinkler protecting the skylight is around 23'-0".
Can I apply the area reduction based on 20'-0" ceiling height? I think I can but I've never had this come up before.
Let me add just to make sure I am on the safe side I'll go with without the area reduction because I like to play safe.