jimmy2times
Electrical
- Jun 26, 2007
- 138
This relates to another recent thread i posted 238-414369
We measured circ current in installation with single corre cables laid in non-trefoil arrangement for 20% of cable run. Breaks out of trefoil then in to groups of three parallel phase conductors per phase with approx 6" between phase groupings at either end of cable run. Circ current measured 130A at part load. Disconnected transformer end ground braiding by disconnecting bolt connection to ground bar and insulating lug end (ground braiding is insulated itself). Cable armour and cable screen individually insulated. Converter end remained grounded
Was end expecting to see little current. Still measured 15A under similar part load? An order lower but expected 1A max. Any ideas?
We measured circ current in installation with single corre cables laid in non-trefoil arrangement for 20% of cable run. Breaks out of trefoil then in to groups of three parallel phase conductors per phase with approx 6" between phase groupings at either end of cable run. Circ current measured 130A at part load. Disconnected transformer end ground braiding by disconnecting bolt connection to ground bar and insulating lug end (ground braiding is insulated itself). Cable armour and cable screen individually insulated. Converter end remained grounded
Was end expecting to see little current. Still measured 15A under similar part load? An order lower but expected 1A max. Any ideas?