Hi all,
Im currently doing a transient analysis pressure surge for firewater system. I have problem in sizing the right Air Release Valve at the highest point of the system.
Comparing 2 cases,
Case 1
when the deluge valve for the largest fire zone is opened, there are large amount of water (1800 m3/hr) will flow out from the system thus creating a vacuum at the highest point. Ive then put the ARV at some point and the surge (due to vacuum formation) is solved. The ARV size is 4"x4" with the orifice size of 6/64" (2.34mm)
Case 2
when two firewater monitors at the helideck are activated, the amount of water flowing out the system is much smaller (270 m3/hr) compare to case 1. By using the same ARV size and location (supposed to), there is high pressure surge happened at the ARV section.
After i change the ARV size from 4"x4" to 1"x1", the surge problem is gone.
So, it looks like Case 1 needs a large ARV and Case 2 needs a small ARV. and there is no size in between is suitable.
Can anybody in here know why is this happening and how to solve it? Really appreciate if you guys can help me. thank you in advance.
Regards,
Fikree
Im currently doing a transient analysis pressure surge for firewater system. I have problem in sizing the right Air Release Valve at the highest point of the system.
Comparing 2 cases,
Case 1
when the deluge valve for the largest fire zone is opened, there are large amount of water (1800 m3/hr) will flow out from the system thus creating a vacuum at the highest point. Ive then put the ARV at some point and the surge (due to vacuum formation) is solved. The ARV size is 4"x4" with the orifice size of 6/64" (2.34mm)
Case 2
when two firewater monitors at the helideck are activated, the amount of water flowing out the system is much smaller (270 m3/hr) compare to case 1. By using the same ARV size and location (supposed to), there is high pressure surge happened at the ARV section.
After i change the ARV size from 4"x4" to 1"x1", the surge problem is gone.
So, it looks like Case 1 needs a large ARV and Case 2 needs a small ARV. and there is no size in between is suitable.
Can anybody in here know why is this happening and how to solve it? Really appreciate if you guys can help me. thank you in advance.
Regards,
Fikree