All,
I would like to start a discussion on the calculation of ''dynamic'' and ''stability'' loads for tower cranes using AS1418.4 in conjunction with manufacturers loads. This in the context of foundation design and checking of lateral deflection for building clearances.
I am posing this question as this is how I have been taught to do it but AS1418 gives no guidance on the use of the different Load Combination numbers and I haven’t found any useful guidance on google. I wanted a verifier that I was interpreting the code correctly.
I would love to get your opinions and suggestions. I have attached excerpt from AS1418.4 to refresh people’s memories.
KEY IS = in service case; OOS = out of service case
LOAD CALCULATION
To get my design loads, I take the manufacturer's loads and multiply by factors to obtain a dynamic moment (IS only); dynamic vertical load (IS only) and stability moments (IS & OOS).
1 – IS dynamic moment calculated by taking the proportion of moment caused by the load on the hook at maximum radius, multiplying by AS1418.4 dynamic factor = 1.3 and then adding this to the manufacturer given static moment.
2 – IS dynamic vertical load calculated by taking the part of the total vertical foundation load caused by the load on the hook, multiplying by AS1418.4 dynamic factor = 1.3 and then adding this to the manufacturers static vertical load.
3 - IS stability moment load calculated by taking all of the manufacturer’s static moment and multiplying by 1.45 (AS1418 Table 2.3.1(A) Out of operation with wind)
4 - OOS stability moment load calculated by taking all of the manufacturer’s static moment and multiplying by 1.2 (AS1418 Table 2.3.1(A) Out of operation extreme wind)
CHECKS
Then when checking the stability & geotechnical capacity of a gravity foundation: IS - I use loads 2&3 for IS loads; OOS – Use load 4 & the raw vertical load for OOS case from manufacturers manual. I check bearing pressure against allowable values.
Then when checking the geotechnical capacity of a piled foundation: IS - I use loads 2&3 for IS loads; OOS – Use load 4 & the raw vertical load for OOS case from manufacturers manual. These are compared against allowable geotech values.
I also take in to account the horizontal loads and any surcharges for all of the stability checks etc.
When checking the lateral sway/deflection of the tower I use the dynamic moment and vertical loads (1&2) for IS and the raw loads for OOS case from manufacturers manual.
For the IS structural strength check I take the dynamic moment and vertical loads and factor in accordance with AS1170. For the OOS structural strength I take the raw manufacturer’s loads and factor in accordance with AS1170.
How do people use the minimum factors of safety against overturning given in AS1418.1 6.2 in conjunction with the AS1418.4, these are given below:
The stability margin (FS) shall be not less than the following values:
(i) Crane in service................................................................................................... 1.4.
(ii) Crane out of service subject to the design wind loading ........................................ 1.2.
I would like to start a discussion on the calculation of ''dynamic'' and ''stability'' loads for tower cranes using AS1418.4 in conjunction with manufacturers loads. This in the context of foundation design and checking of lateral deflection for building clearances.
I am posing this question as this is how I have been taught to do it but AS1418 gives no guidance on the use of the different Load Combination numbers and I haven’t found any useful guidance on google. I wanted a verifier that I was interpreting the code correctly.
I would love to get your opinions and suggestions. I have attached excerpt from AS1418.4 to refresh people’s memories.
KEY IS = in service case; OOS = out of service case
LOAD CALCULATION
To get my design loads, I take the manufacturer's loads and multiply by factors to obtain a dynamic moment (IS only); dynamic vertical load (IS only) and stability moments (IS & OOS).
1 – IS dynamic moment calculated by taking the proportion of moment caused by the load on the hook at maximum radius, multiplying by AS1418.4 dynamic factor = 1.3 and then adding this to the manufacturer given static moment.
2 – IS dynamic vertical load calculated by taking the part of the total vertical foundation load caused by the load on the hook, multiplying by AS1418.4 dynamic factor = 1.3 and then adding this to the manufacturers static vertical load.
3 - IS stability moment load calculated by taking all of the manufacturer’s static moment and multiplying by 1.45 (AS1418 Table 2.3.1(A) Out of operation with wind)
4 - OOS stability moment load calculated by taking all of the manufacturer’s static moment and multiplying by 1.2 (AS1418 Table 2.3.1(A) Out of operation extreme wind)
CHECKS
Then when checking the stability & geotechnical capacity of a gravity foundation: IS - I use loads 2&3 for IS loads; OOS – Use load 4 & the raw vertical load for OOS case from manufacturers manual. I check bearing pressure against allowable values.
Then when checking the geotechnical capacity of a piled foundation: IS - I use loads 2&3 for IS loads; OOS – Use load 4 & the raw vertical load for OOS case from manufacturers manual. These are compared against allowable geotech values.
I also take in to account the horizontal loads and any surcharges for all of the stability checks etc.
When checking the lateral sway/deflection of the tower I use the dynamic moment and vertical loads (1&2) for IS and the raw loads for OOS case from manufacturers manual.
For the IS structural strength check I take the dynamic moment and vertical loads and factor in accordance with AS1170. For the OOS structural strength I take the raw manufacturer’s loads and factor in accordance with AS1170.
How do people use the minimum factors of safety against overturning given in AS1418.1 6.2 in conjunction with the AS1418.4, these are given below:
The stability margin (FS) shall be not less than the following values:
(i) Crane in service................................................................................................... 1.4.
(ii) Crane out of service subject to the design wind loading ........................................ 1.2.