asixth
Structural
- Feb 27, 2008
- 1,333
Hi team
I had a minor dispute with a builder on-site yesterday regarding the position of HD rods in plywood bracing walls. Reading through AS1684 it says that an M12 rod must be located at either end of a plywood bracing wall, and then shows an indicative illustration of the M12 rod located within the end of the plywood panel.
I saw on-site that the builder had located one of the tie down rods slightly outside the sheathed wall. I mentioned that the rod needs to be within the sheathed section of wall. The response from the builder was that the "rules" are that the rod can be +/- 100mm from the end of the sheathing. I couldn't find anywhere in AS1684 where it says that this is the case.
I would have thought that the HD rod must be located within the panel because the sheathing acts as the structural element. If the rod is located outside the panel then the top plate will need to work in weak axis bending. I know that a 90x45 on it's flat won't be able to transfer a 13kN hold down force.
While we are on the topic of AS1684. What is everyone's opinion on using the standard details and accompanying capacites in AS1684 for buildings other than houses (ie. not Class 1 or 10 buildings as defined in the BCA).
I know when these connections are solved from first principles (AS1720) that the capacity of the connection will be less than what is stated in AS1684. Also AS1720 has greater capacity reduction factors for structurs "other than houses" than it does for "houses".
What are others doing, are they using AS1684 for buildings other than Class 1 or 10 and where should the location of the hold down rod be when using the detail in Table 8.18(h) Method A?
All opinions are welcomed.
I had a minor dispute with a builder on-site yesterday regarding the position of HD rods in plywood bracing walls. Reading through AS1684 it says that an M12 rod must be located at either end of a plywood bracing wall, and then shows an indicative illustration of the M12 rod located within the end of the plywood panel.
I saw on-site that the builder had located one of the tie down rods slightly outside the sheathed wall. I mentioned that the rod needs to be within the sheathed section of wall. The response from the builder was that the "rules" are that the rod can be +/- 100mm from the end of the sheathing. I couldn't find anywhere in AS1684 where it says that this is the case.
I would have thought that the HD rod must be located within the panel because the sheathing acts as the structural element. If the rod is located outside the panel then the top plate will need to work in weak axis bending. I know that a 90x45 on it's flat won't be able to transfer a 13kN hold down force.
While we are on the topic of AS1684. What is everyone's opinion on using the standard details and accompanying capacites in AS1684 for buildings other than houses (ie. not Class 1 or 10 buildings as defined in the BCA).
I know when these connections are solved from first principles (AS1720) that the capacity of the connection will be less than what is stated in AS1684. Also AS1720 has greater capacity reduction factors for structurs "other than houses" than it does for "houses".
What are others doing, are they using AS1684 for buildings other than Class 1 or 10 and where should the location of the hold down rod be when using the detail in Table 8.18(h) Method A?
All opinions are welcomed.