Hi everyone!

I am designing some steel latticed structures for an electrical substation using ASCE 10-15.

I have some pretty dumb doubt. The specification dosen´t show any load combinations and I can't find any resistance factors neither. It does however mention "Desing-factored loads"in 2.2.

Should LRFD load combinations and AISC resistance factors be used ?(0.9 for compression for example).

I tried designing a stocky column in compression according to ASCE 10-97 in sap2000 and it seems it is not considering any resistance factor (0.9), the required strength is just checked against yielding without any factor, Pc=A*Fy (no 0.9.

There will be other elements in the same project designed with AISC 360-16 so it seems weird applying different resistance fators in different structures.

Thanks!



 
Replies continue below

Recommended for you

Section C2.1 Introduction mentioned that your load factors are taken from the IEEE

For resistance factors I stick with AISC 360 unless it is already applied (as per C3.15) or noted otherwise

 