ASCE 37-02 Construction Wind Loads

Status
Not open for further replies.

pcronin

Structural
Nov 15, 2002
53
I am designing an exterior temporary construction wall (38'6" tall). The wall may be in place for quite some time (6-12 months) so I was designing using components and cladding wind loads from ASCE 7-05. My office does not have a copy of the ASCE 37-02 "Design Loads on Structures During Construction". I ordered the book today, but I the project may not have the time to wait for it. My questions are as follows:

1. Does the ASCE 37-02 cover wind loads? What is the maximum duration that they allow a structure to remain and still be considered "temporary construction"?

2. If I have a wind speed of 100 mph, exposure C, Aeff = 500 psf, gamma of 1.49 (Rh=40'), what type of reduction in the wind load would I expect? Is it worth taking this reduciton? Right now the interior C&C wind load is 14.9*1.49 = 22.2 psf.

Thanks for your help.
 
Replies continue below

Recommended for you

ASCE 37-02 has you reduce the design wind speed based on your construction period. For a period of 6 weeks to 1 year, the reduction factor is 0.8. So your 100 mph wind speed would become 80 mph. Use that speed in the ASCE 7 equations to calculate your wind pressure. The speed gets squared, so your wind pressures would be reduced by 0.64.
 
exactly what I was looking for. Thanks.
 