If I have a Type 4 Irregularity - Re-Entrant corner, the code states I can't use the Simplified Wind Load method because of the stipulation in 6.4.1.1. This method uses the zones labeled in Figure 6.2 and pressures in the following tables. However, I specifically remember my professor leading us through that procedure on an L-shaped building (re-entrant corner). Was that the wrong method to use or does one of the other procedures follow the same tables? I know that we had to design the drag strut and collector through the re-entrant corner, but everything else followed simplified method. We did break up the building to have two "a" zones on the outside corners. Any insight would be appreciated.
 
Replies continue below

Recommended for you

If you read ASCE 7-05 section C6.2 on this, you will find a "L" shape building will be able to be designed with the Figs 6-6 to 6-17.

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
 
Does that mean my professor was wrong in using the tables in Figure 6-2 to calculate the wind loads for this building? Both Methods 1 and 2 list that they are only to be used for buildings that are regular. Certainly we don't use the wind tunnel method for any building that has any irregularity...?
 
Do not know what your building actually looks like. But if section 6.4.1.1 note 8 is not a problem than usually the building can be considered regular. I suggest you read Chapter C6 and form your own opinion for your structure.

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
 
Maybe I am overthinking the code. Correct me if I am wrong, but the only description of a "regular-shaped building" is in 6.2, where it states that a regular-shaped building is one "having no unusual geometrical irregularity in the spatial form." However, when I am looking in the seismic area of the code it talks about structural irregularities in table 12.3-1. Am I considering a re-entrant corner an irregularity in seismic, where in wind it would be considered a regular-shaped building? Otherwise, 99% of the buildings out there are irregular in my mind for some reason or another.
 
Sorry, I initially said it was a Type 4 irregularity, but it is actually a Type 2 (L-shaped building).
 