- 2,759
I am in the process of designing a single-story building that is 225’ x 200’ with 56’ x 40’ bays. Mean roof height = 30’-0”. The building is to be designed in accordance with IBC 2015/ASCE7-10. Wind speed is 130 mph. Monoslope roof with pitch = 1/4"/foot The building is to utilize steel decking, open-web steel joists and joist girders.
I am now in the process of trying to design the foundations. I need check the foundations on the interior footings for uplift due to roof suction. Section 30.2.3 of ASCE 7 says if the area of the component is greater than 700 square feet then you shall be permitted to design the member using the provisions of the MWFRS (interior footings are supporting 2,000+ square feet of roof).
So am I am to follow this correction I can use equation 27.4-1 using the roof pressure coefficients of figure 27.4-1?
This method seems to reduce the wind uplift loads significantly as you get towards the center of the building as Cp reduces from a maximum of -0.9 at the perimeter(0'-0" to 30'-0" in), to -0.5 (30'-0" to 60'-0"), to -0.3 in the center (60’-0” away from the edge of the building).