EngineerRam
Structural
Per ASCE 7, a partially enclosed structure is defined as such:
1. The total openings in a wall exceeds the sum of the areas of openings in the balance of the building
envelope by >10%.
2. The total area of openings in a wall that receives positive external pressure exceeds 4ft2 or 1% of
area of that wall, and the percentage of openings in the balance of the building envelope ≤ 20%.
I am in a situation where I can go from partially enclosed to enclosed by increasing my openings in the building shell.
If my total openings in any wall is greater than 10% of the openings in the balance of the building, I add openings to the roof, or walls with less openings so that condition 1 is not satisfied. Because 1 is not satisfied and both need to be satisfied for it to be partially enclosed, I can assume the building is enclosed(as all walls are not 80% open).
This seems illogical and counterintuitive, however I don't believe I am violating any provisions in the ASCE by doing this. Can anyone provide any reasoning as to why this is?
Thanks
1. The total openings in a wall exceeds the sum of the areas of openings in the balance of the building
envelope by >10%.
2. The total area of openings in a wall that receives positive external pressure exceeds 4ft2 or 1% of
area of that wall, and the percentage of openings in the balance of the building envelope ≤ 20%.
I am in a situation where I can go from partially enclosed to enclosed by increasing my openings in the building shell.
If my total openings in any wall is greater than 10% of the openings in the balance of the building, I add openings to the roof, or walls with less openings so that condition 1 is not satisfied. Because 1 is not satisfied and both need to be satisfied for it to be partially enclosed, I can assume the building is enclosed(as all walls are not 80% open).
This seems illogical and counterintuitive, however I don't believe I am violating any provisions in the ASCE by doing this. Can anyone provide any reasoning as to why this is?
Thanks