ASCE 7 Section 7.3.4 (Min. pf) 2

Status
Not open for further replies.

STR04

Structural
Jun 16, 2005
187
A bldg 20'x40' with a hip roof on a 3:12 slope shall use what pf (min) according to 7.3.4? My pg=50psf so this really hurts me if I have to use pf=50psf. I want to say use the ps=Cspf (Eq. 7-2) but I've seen others use pf=pg. Since my 3:12 slope equates to 14.03 degrees which is greater then (70/W)+0.5=7.5 then do I go to Section 7.4 (eq. 7-2) ps=Cspf or use the pf=50psf? My slope is less than the minimum 15 degrees but it says for monoslope roofs. Please help.

TIA
 
Replies continue below

Recommended for you

STR04
Since no one answered you,I'll give it a try.
This is the way I read it;

Eq.7-1 Flat Roof Snow Load:
pf = 0.7(Ce)(Ct)(I)(pg) where pg = 50psf
but not less than 20(I)

Your slope(hip roof) is 14.03 deg. which is greater than (70/W) + 0.5 = 7.5
Therefore use Eq. 7-2 Sloped Roof Snow Load:
ps = (Cs)(pf)
where pf is from Eq. 7-1 above.

Why use pf = pg?
 
warrenw,
To answer your question, some local building department offices require it. I recently did a project in Douglas County, CO (near Denver) where they required that pf = pg.
 
Thank you both for the clarification. Then based upon ASCE 7 section 7.3,7.4 your load can only be one of the following three choices whether it’s flat, hip or gable:

1) pf=0.7CeCtIpg
2) pf=Ipg or 20I
3) ps=Cspf

This does not include pf=pg unless your local building official requires this. Agree or not?

 