Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

ASCE-7 Seismic requirements for small buildings & structures

Status
Not open for further replies.

Bagman2524

Structural
Jul 14, 2005
706
I design industrial platforms and other small (less than 2 stories or 20 ft high) structures. Am I correct in interpreting ASCE-7-98 section 9.5.2.5 exceptions 1 & 2 as not requiring any type of seismic loading to be considered in the design of these structures?
 
Replies continue below

Recommended for you

I believe that if you kept reading that section, you will find that you are permitted to use the SIMPLIFIED method of analysis per para 9.5.3.8 and your structure should be in Seismic Use Group I. You are not exempt from seismic analysis in any event.

By the way, you should be using ASCE 7-05. Your reference is two editions old.
 
Thanks. I agree.
Keeping up with the latest versions of all codes and standards I need to gets to be expensive.
 
Out of date standards could cost you dearly when subjected to plan review by third party engineers.
 
But what if your state code refers to an old state (such as new york city).
 
My software uses the current edition of the code.
 
The simplified seismic base shear and such is now in Chapter 12 of ASCE 7. Seismic gets chapters 9 through 22 now!
 
There was a post a while back on the topic of current standards. Typically a city will specify an edition of IBC, and it in turn will specify an edition of ASCE 7. Last one I looked at, city specced IBC 2000, which references ASCE 7-98. But it does vary.
 
Chapter 1 of IBC allows for alternate forms of compliance and most jurisdictions accept newer referenced standards. MAke sure your submittal drawings indicate the standard to help protect yourself.

However, if there is a less stringent item in the current standard compared to the older, the building official may require you to adjudicate the requirement to protect himself from liability. Most building officials would support the variance request since future codes will probably incorporate the new requirement.

Don Phillips
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor