ASCE 7 wind load

Status
Not open for further replies.

Wbruseski

Structural
Jul 18, 2001
18
US
What is the correct way for calculating the wind load on the overhang using ASCE 7? I have gotten conflicting opinions about using the overhang wind load or adding the overhang wind load to the roof load.
 
Replies continue below

Recommended for you

I interpret ASCE 7-95 for overhang design to be investigated as 1)components and cladding 2)part of the transfer into the MWFRS

For the second part, I would take pressure to the bottom of the windward overhang (w/Cp=+0.8) in addition to the values given in Fig 6-3 & 6-4 applied to topside of overhang/roof.
Leeward overhang treated as part of leeward roof. Be careful for a roof with a slope>30 degrees.
 