TBacon
Structural
- Jul 24, 2007
- 15
I mostly work with small scale construction, rarely encountering buildings over two stories tall. I would like to know which wind design methodology people use and in particular why. Does one method tend to give you more conservative, or more accurate results over the others, again when considering the design for smaller scale buildings? In an effort to understand the different results obtained from the various wind design approaches I ran the numbers on a simple, single story building, with a flat roof with the following criteria and came up with a fairly wide range of design wind pressures for the walls (all calc'd / converted to an ASD force level). My sample building is enclosed, has a simple diaphragm, and so as I understand it the internal pressure coefficient, (GCpi) is equal to zero.
Building dimensions: 80' x 30' x 14' tall oriented with the long dimension facing north/south
Risk Category II
Vult - 110 mph
Exposure Category 'C'
IBC 1609.6.3 P = 15 psf (in both directions)
Chapter 27 Part 1 P = 14.8 psf N/S & P = 12 psf E/W
Chapter 27 Part 2 P = 21 psf N/S & P = 12 psf E/W
Chapter 28 Part 1 P = 13.4 psf N/S & P = 10 psf E/W
Chapter 28 Part 2 P = 14 psf (in both directions)
Building dimensions: 80' x 30' x 14' tall oriented with the long dimension facing north/south
Risk Category II
Vult - 110 mph
Exposure Category 'C'
IBC 1609.6.3 P = 15 psf (in both directions)
Chapter 27 Part 1 P = 14.8 psf N/S & P = 12 psf E/W
Chapter 27 Part 2 P = 21 psf N/S & P = 12 psf E/W
Chapter 28 Part 1 P = 13.4 psf N/S & P = 10 psf E/W
Chapter 28 Part 2 P = 14 psf (in both directions)