mmcdonal143
Civil/Environmental
- Feb 6, 2008
- 2
Does ASHRAE 135 (controls spec) make any provisions for a "change-over" delay when switching a VAV terminal unit from heating to cooling or vice versa?
This seems like a common sense practice, to prevent short-cycling, but I'm getting some resistence from the client and they're saying that it is not spec'd.
When a room VAV with a reheat coil and supplemental radiant ceiling panel heating is in heating mode:
1. VAV is at min CFM
2. Reheat & Radiant Heat valves are open
Switch to cooling mode -->
1. Reheat & Radiant heat valves close
2. 5 (or whatever number you choose) minute change-over delay.
3. VAV opens to max CFM
My questions are:
a. Does this time delay make sense?
b. Is this time delay prescribed somewhere in ASHRAE?
This seems like a common sense practice, to prevent short-cycling, but I'm getting some resistence from the client and they're saying that it is not spec'd.
When a room VAV with a reheat coil and supplemental radiant ceiling panel heating is in heating mode:
1. VAV is at min CFM
2. Reheat & Radiant Heat valves are open
Switch to cooling mode -->
1. Reheat & Radiant heat valves close
2. 5 (or whatever number you choose) minute change-over delay.
3. VAV opens to max CFM
My questions are:
a. Does this time delay make sense?
b. Is this time delay prescribed somewhere in ASHRAE?