PSSC
Mechanical
- Feb 11, 2008
- 63
I have been in the process of revamping several process piping systems that need to be hydro tested.
I have the original drawings with the hydro test pressures.
They do not seem to take into account the prevision of not exceeding the yield strength of the material at the test temperature.
I have always used the values from Table A-1.
Specifically the value of "Min Temp to 100", for the test temperature strength.
This is usually lower than the "Specified Min. Strength".
Am I using the correct value?
If I used the higher value I think the original hydro test values would be acceptable.
If not I am guessing no one paid attention to this part of the code.
What is the customary value to use?
Thanks in advance.
I have the original drawings with the hydro test pressures.
They do not seem to take into account the prevision of not exceeding the yield strength of the material at the test temperature.
I have always used the values from Table A-1.
Specifically the value of "Min Temp to 100", for the test temperature strength.
This is usually lower than the "Specified Min. Strength".
Am I using the correct value?
If I used the higher value I think the original hydro test values would be acceptable.
If not I am guessing no one paid attention to this part of the code.
What is the customary value to use?
Thanks in advance.