ASME SEC I, SAFETY RELIEF VALVE

Status
Not open for further replies.

mihir5577

Mechanical
Jun 10, 2005
42
HI,
I WANT TO KNOW THAT, CAN WE USE TWO SAFETY RELIEF VALVE FROM ONE CONNECTION ON TOP DRUM BY USING TEE OR ANY OTHER FITTINGS, FOR HIGH STEAM BOILER[ABOVE 500 SQ. FT HTG. SURFACE AND ABOVE 4000LB/HR STEAM GEN. CAP.]?
IF YES I WANT TO KNOW PARA NO. FROM ASME SECTION I.
I WANT RESPONSE VERY VERY FAST PLS.....
THANKS IN ADVANCE
M.B.S
 
Replies continue below

Recommended for you

Review PG-71 in Section I. Two valves may be used on "Y" fitting but they must be independent of each other.
 
HI,
THANKS FOR PROMPT REPLY.
BUT COULD U PLS. EXPLAIN ME THAT "Y" FITTINGS MEANS?
AND INDEPENDENT OF EACH OTHER MEANS?
PLS...EXPLAIN ME....
THANKS IN ADVANCE
M.B.S.
 
It sounds like you don't have a copy of ASME Section I??? If you do have a copy, the words are there for your guidance.
 
Hi,
What are the requirements for the connecting piping of the two (2) relief valves to one boiler pressure vessel opening?
Is there any calculation required to show an A.I?
pls. advice me asap.
thanks
M.B.S
 
mihir5577 Yee eans a Yee type of tee,
simple enough you choose a yee because a std tee will accumulate water so a yee and 2 niples and couplings will separate the 2 sv's from each other
consult your plumbing books or the supplier and they will know you will see.

genb
 
you will also need to confirm the reactions from the releif valve will not overtune or damage the wye connection- this might be done by placing a saddle support under the valves.
 
Status
Not open for further replies.