- Aug 12, 2008
- 9
I am trying to determine whether a relief valve is required on a vessel due to planned pump upgrades. The pump motor and impeller upgrades in question will generate pressures only 5% greater than the vessel design pressure for the blocked outlet case.
UG-140(b): "If the pressure is not self-limiting, a pressure vessel may be protected from overpressure by system design or by a combination of overpressure by system design and pressure relief devices, if the following conditions are met."
Condition 1 states "The vessel is not exclusively in air, water, or steam service"
Does anyone know why water is excluded? The process fluid I am working with is Seawater - is this excluded as well?
UG-140(b): "If the pressure is not self-limiting, a pressure vessel may be protected from overpressure by system design or by a combination of overpressure by system design and pressure relief devices, if the following conditions are met."
Condition 1 states "The vessel is not exclusively in air, water, or steam service"
Does anyone know why water is excluded? The process fluid I am working with is Seawater - is this excluded as well?