Dear Friends,
We have Project specifying asphalt wearing course 50mm thick average laid over concrete deck (350mm thick). Between the two there lies a 4mm thick torch applied waterproofing membrane. Now, when you apply the membrane to the concrete and lay hot-mix asphalt wearing course 50mm average thick, the follwoing problems are encountered,
1. Due to air-packets between the concrete and the membrane the asphalt gets cracked from below since the air trying to expel the asphalt outwards. This is due to improper application of the membrane.
2. The structure is a marine jetty, where 50 tonnes capacity crane manouver to load and unload stuff. Due to such heavy static loads of cranes and forklifts, the wearing course is getting scaled-off or peeled-off below the tyres of such equipments.
3. The entire area of arphalt is deteriorated within 4 months of laying due to above reasons.
We are in serious trouble and tried check the marshall properties of the laid asphalt. The results match with the specs, stability and loss of stability is ok. This problem is only at the areas above the concrete deck and not where we have laid the same asphalt over aggregate base course. We reckon following may be the reasons for failure,
a. Separation layer of membrane causing debonding between the asphalt and concrete. Air packets is the main reason.
b. Lesser thickness of asphalt for such loading.
Can somebody help us please.
We have Project specifying asphalt wearing course 50mm thick average laid over concrete deck (350mm thick). Between the two there lies a 4mm thick torch applied waterproofing membrane. Now, when you apply the membrane to the concrete and lay hot-mix asphalt wearing course 50mm average thick, the follwoing problems are encountered,
1. Due to air-packets between the concrete and the membrane the asphalt gets cracked from below since the air trying to expel the asphalt outwards. This is due to improper application of the membrane.
2. The structure is a marine jetty, where 50 tonnes capacity crane manouver to load and unload stuff. Due to such heavy static loads of cranes and forklifts, the wearing course is getting scaled-off or peeled-off below the tyres of such equipments.
3. The entire area of arphalt is deteriorated within 4 months of laying due to above reasons.
We are in serious trouble and tried check the marshall properties of the laid asphalt. The results match with the specs, stability and loss of stability is ok. This problem is only at the areas above the concrete deck and not where we have laid the same asphalt over aggregate base course. We reckon following may be the reasons for failure,
a. Separation layer of membrane causing debonding between the asphalt and concrete. Air packets is the main reason.
b. Lesser thickness of asphalt for such loading.
Can somebody help us please.