I have a project that had ASTM A193 grade 8B Class 2 stainless steel threaded rods specified for a concrete corbel repair but Class 1 was installed . The connection is now covered with grout with a beam on the corbel. My understanding is that the only difference between the class 1 & 2 is strain hardening. The rods are subjected to direct tension only.
Class 1 Fy = 30 ksi
Class 2 Fy = 100 ksi
What is involved with Strain Hardening and as the load on this corbel increases, will it in effect be "strain hardened"?
Class 1 Fy = 30 ksi
Ftu = 75 ksiClass 2 Fy = 100 ksi
Ftu = 125 ksiWhat is involved with Strain Hardening and as the load on this corbel increases, will it in effect be "strain hardened"?