Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

ASTM C680 Calculator

Status
Not open for further replies.

IanVG

Mechanical
Jan 21, 2022
76
Hey everyone,

Does anyone know of a calculator based off the ASTM C680 standard? I would like to calculate the temperature gain over a run of ductwork. the formula listed in the ASHRAE HoF is t_gain = 0.2*[(q*P*L)/(V*C_p*row*A)], where the terms are:

* q = heat loss through duct wall (Btu/hr*ft^2)
* P = duct perimeter (in)
* L = length of duct run (ft)
* V = air velocity (ft/min)
* C_p = specific heat of air (Btu/lbm*F°)
* row = density of air (0.075 lb/ft^3)
* A = area of duct (in^2)
* 0.2 = conversion factor for length and time units

I understand how to calculator/estimate all the variables except q (heat loss through duct wall). The handbook vaguely recommends that I use a calculator/calculation based off the ASTM standard C680. When I internet search calculators based off the ASTM standard C680, I don't find any hits. Does anyone have any recommendations or help?
 
Replies continue below

Recommended for you

I'm not sure of a calculator for this. This would be a heat transfer problem, I believe the equation that might work for you is:

Q=hA(T-T_inf)
Q=BTU/hr
A=surface area (square ft)
T=temperature of air inside the duct at specific point (°F)
T_inf=temperature of the air around the duct (°F)
h=convection heat-transfer coefficient (BTU/hr-sq.ft-°F) (this is a little difficult to find)

Then you could use that Q value to find the t_gain that you're looking for over a short distance, then just iterate. That's how I'd start looking at it at least.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor