Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

ATS for two 240V 100A services, no generator

Status
Not open for further replies.

sasart

Chemical
Feb 16, 2001
1
0
0
US
I want to find and purchase two automatic transfer switches so two 240V 100A supplies can back each other up. No generator is used, so I don't need generator controls or time delays.
 
Replies continue below

Recommended for you

Just use a regualr ATS and only feature you will not be using ise generator start/stop singals.

But you still need timer fortransferring back and forth after adequate time delays to see the voltage/freq is stable after return of a source. Also you want to make sure that the outage is permannet (not momentary dip) before you tranfer to other source.

Plus a standard product will maintain UL listing etc...

Sometime it costs more to remove features too..
 
Status
Not open for further replies.
Back
Top