syarn
Structural
- Sep 10, 2008
- 27
does 2007 nfpa 13 section 8.15.1.2 offer exceptions from sprinkling an attic?
for example, 2007 nfpa 13, section 8.15.1.2.2 says concealed spaces of noncombustible and limited-combustible construction with limited access and not permitting occupancy or storage of combustibles shall not require sprinkler protection. the space shall be considered a concealed space even with small openings such as those used as return air for a plenum.
Would a wood roof truss and plywood roof deck framing such an attic be considered “noncombustible” or “limited-combustible”?
for example, 2007 nfpa 13, section 8.15.1.2.2 says concealed spaces of noncombustible and limited-combustible construction with limited access and not permitting occupancy or storage of combustibles shall not require sprinkler protection. the space shall be considered a concealed space even with small openings such as those used as return air for a plenum.
Would a wood roof truss and plywood roof deck framing such an attic be considered “noncombustible” or “limited-combustible”?