SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,261
I have a cold storage warehouse with a double interlocked preaction system where I plan to use a water storage tank and fire pump. Pump will be rated at 1,500 or2,000 gpm.
Flow test results of the city watermain show 68 psi static, 42 psi residual @ 993 gpm. 20 psi @1,400 gpm.
500gpm hose stream demand will be from city hydrants.
Storage is a Class II commodity consisting of nonencapsulated frozen chicken in multiple row racks per Figure 21.4.1.2(b) which requires a density of .55/2,600 after applying Figure 21.4.1.4.1.
Theoretically the minimum discharge is 0.546x2,600=1,419.6 gpm but my preliminary calculations indicate I will need 1,850 gpm.
There will not be any hydrants downstream the fire pump and tank.... hose stream demand of 500 gpm will be obtained from the city water main.
For a 2 hour supply it appears I will need a stored water tank having 120*1,850=222,000 gallons.
What a difference multiple row racks make!
Anyway, I have calculations that show if I install a 6" fill line with an automatic fill valve https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/17388-source/es-acv-f100-f1100-pdf I shouldn't have a problem automatically filling the tank at 800 gpm given the city water supply we have. The fill valves are not UL:/FM nor do they have to be since they are not directly supplying the sprinklers.
In two hours we could replace 800*120=96,000 gallons which would lower my tank size to 126,000 gallons saving a bit of money.
Let's face it, installing tanks isn't something we do every day and I seem to remember the last one I did was an FM job and FM would allow the fill valve only if TWO (2) fill valves were used. It was some time ago so it could have changed.
Why the 1,500 gpm pump? I am giving the owner the option, which is his choice, to limit the height of storage to 20'-0" because it is surprising the extra water required that 2'-0" will require with multiple row racks. With 20' high storage the design is .42/2,600 which my preliminary calculations indicate I will been 1,400 gpm which , with the full valve at 800 gpm, would reduce the tank size to 96,000 gallons.
Overhead sprinkler pipe size is crazy. I am going to go with three systems covering 48,000 sq ft just to make sure I can meet the 60 second trip time.
Anyone have any input it would be most appreciated.
Flow test results of the city watermain show 68 psi static, 42 psi residual @ 993 gpm. 20 psi @1,400 gpm.
500gpm hose stream demand will be from city hydrants.
Storage is a Class II commodity consisting of nonencapsulated frozen chicken in multiple row racks per Figure 21.4.1.2(b) which requires a density of .55/2,600 after applying Figure 21.4.1.4.1.
Theoretically the minimum discharge is 0.546x2,600=1,419.6 gpm but my preliminary calculations indicate I will need 1,850 gpm.
There will not be any hydrants downstream the fire pump and tank.... hose stream demand of 500 gpm will be obtained from the city water main.
For a 2 hour supply it appears I will need a stored water tank having 120*1,850=222,000 gallons.
What a difference multiple row racks make!
Anyway, I have calculations that show if I install a 6" fill line with an automatic fill valve https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/17388-source/es-acv-f100-f1100-pdf I shouldn't have a problem automatically filling the tank at 800 gpm given the city water supply we have. The fill valves are not UL:/FM nor do they have to be since they are not directly supplying the sprinklers.
In two hours we could replace 800*120=96,000 gallons which would lower my tank size to 126,000 gallons saving a bit of money.
Let's face it, installing tanks isn't something we do every day and I seem to remember the last one I did was an FM job and FM would allow the fill valve only if TWO (2) fill valves were used. It was some time ago so it could have changed.
Why the 1,500 gpm pump? I am giving the owner the option, which is his choice, to limit the height of storage to 20'-0" because it is surprising the extra water required that 2'-0" will require with multiple row racks. With 20' high storage the design is .42/2,600 which my preliminary calculations indicate I will been 1,400 gpm which , with the full valve at 800 gpm, would reduce the tank size to 96,000 gallons.
Overhead sprinkler pipe size is crazy. I am going to go with three systems covering 48,000 sq ft just to make sure I can meet the 60 second trip time.
Anyone have any input it would be most appreciated.