Automatic Transfer Switch

Status
Not open for further replies.

sv879

Mechanical
Dec 7, 2018
68
Dear Experts,

A multi story building with 45 floor wherein a technical floor at 22nd floor. As per the specified requirement wanted to keep 2 electric (ie, 1 duty & 1 standby) + 1 jockey pump. Since two electric pumps, Automatic Transfer Switch is required.

The query is : whether both the pumps (ie, 1 duty & 1 standby) required to be provided Automatic Transfer Switch or it is required for only one pump?

Project location: UAE.

Appreciate your thoughts and comments on this.
 
Replies continue below

Recommended for you

What does the UAE code prescribe? I'm unsure why the 22nd floor is relevant to this question. Is this a very tall building as described in NFPA 20?
 
22nd floor is irrelevant, It is a very tall building as per NFPA 20, and super high rise building as per UAE FC.
UAE fire code prescribe as follows:

Untitled_hwnvui.png
 
A listed ATS is required for each fire pump. If two electric fire pumps are specified, item 8 section ii conflicts with NFPA 20 because the ATS must be an integral element of the fire pump controller, and it's a really bad idea to do so because of National Electrical Code Article 695. However, this is a UAE regulation so they may want something different.
 

I didn't find any conflict with NFPA 20.
As per NFPA 20, ed 2019 : ATS shall be either listed combination of fire pump controller and power transfer switch / individually listed fire pump controller and transfer switch.

I am not familiar with NEC. Is there any clause which make conflict with UAE regulation. Kindly share.
 
Any input on this thread much appreciated. Thank you.
 