Hi RonShap & Alehman,
I've got a similar problem with a transfer scheme with two 'utility' feeds and a standby genset. The utility feeds are from our own internal 11kV network and are solid-grounded to the site earthing grid. All three feeds are 4-pole ACB's equipped with a mid-range protection unit using CTs on all four conductors to provide a residual connection for ground fault detection, plus the usual functions for IDMT and instanaeous trip. Line-neutral loads are present, so the neutrals must be solidly connected to earth to meet British regs.
The genset has the ability to synch to either utility for a closed transfer, or to synch and run in parallel with one of the utility feeds to provide an on-load test facility. In this mode our ground fault protection is compromised because the neutrals of utility feeds and genset are both connected to the site earthing grid at points remote from each other, thus creating a low-impedance path through the earth grid in parallel with the neutral conductor.
I'm sure there is solution to this, but I'm scratching my head at the moment. I don't want to desensitise the earth fault protection because it seems a very crude solution and will screw up coordination elsewhere. Has anyone an off-the-shelf solution to this which they have used before?
TIA for any assistance.
----------------------------------
If we learn from our mistakes,
I'm getting a great education!