Mbrooke
Electrical
- Nov 12, 2012
- 2,546
Is it physically possible for a major increase in fault current at one substation to actually cause fault current to drop at another nearby?
Here is the scenario. From a 500/345/115kv substation (I will call this substation "A") emanate several 115kv lines which travel about 12 miles to substation "B" From substation "B" 115kv lines travel about 15 miles to substation "C".
For variety of factors a new 345kv lines is being proposed from substation A to another one some distance away. Substation B will tap this new 345kv line, and via a 600MVA transformer connect to the 115kv bus inside substation B.
When all is said and done, computer simulation shows that fault current actually drops at substation C despite there being a good increase at B and even some at A. All the 115kv lines between A, B and C are identical in conductor size and configuration.
Here are the numbers as they are now...
Substation A:
345kv; 31,560 amps --- X/R of 19.5
115kv; 42,700 amps --- X/R of 26
Substation B:
115kv; 12,360 --- X/R of 8.7
Substation C:
115kv; 7460 --- X/R of X/R 11.5
With the 345kv additions...
Substation A:
345kv; 31,645 --- X/R of 19.3
115kv; 45,440 --- X/R of 24.4
Substation B:
345kv autotrafo breaker; 22,800 X/R of 17.2
115kv; 21,815 X/R of 21.7
Substation C:
115kv; 6150 X/R of 12.5
Here is the scenario. From a 500/345/115kv substation (I will call this substation "A") emanate several 115kv lines which travel about 12 miles to substation "B" From substation "B" 115kv lines travel about 15 miles to substation "C".
For variety of factors a new 345kv lines is being proposed from substation A to another one some distance away. Substation B will tap this new 345kv line, and via a 600MVA transformer connect to the 115kv bus inside substation B.
When all is said and done, computer simulation shows that fault current actually drops at substation C despite there being a good increase at B and even some at A. All the 115kv lines between A, B and C are identical in conductor size and configuration.
Here are the numbers as they are now...
Substation A:
345kv; 31,560 amps --- X/R of 19.5
115kv; 42,700 amps --- X/R of 26
Substation B:
115kv; 12,360 --- X/R of 8.7
Substation C:
115kv; 7460 --- X/R of X/R 11.5
With the 345kv additions...
Substation A:
345kv; 31,645 --- X/R of 19.3
115kv; 45,440 --- X/R of 24.4
Substation B:
345kv autotrafo breaker; 22,800 X/R of 17.2
115kv; 21,815 X/R of 21.7
Substation C:
115kv; 6150 X/R of 12.5