jimmy2times
Electrical
- Jun 26, 2007
- 138
I’d like to gauge opinion on following, we have a MV motor (bow thruster on ship), 2MW 6.6kV. Due to poor original system design we have issue with voltage drop on starting across ship when on min generators. Temporary work around being bring more capacity online to start motor. Anyway we are looking to install AT starter as a fix.
Currently the DOL starting uses VCB at switchboard that is approx 200m from motor. Now, due to lack of space in switchroom, looking to install starter more locally to motor. What are views on incorporating fuse in the local starter or just omitting it and keeping the VCB for short circuit protection.
I quite like the idea of remaining fuseless (time to replace and safety) but also thought the fuse would be of some benefit in event of fault (less stress, arc damage in situ). Possibly an unnecessary cost though. There is no existing diff protection.
Control cables need to be run between the two locations regardless of which way we go.
Would it be simplist solution for VCB to clear the overload faults as well? Or leave that locally to contactor?
(Still wondering if it is feasible to replace the VCB with fused softstarter but waiting for switchboard OEM to advise on that), that could be another topic in itself though. Think it is a non-starter (excuse the pun!) due to space though.
Thanks as always.
Currently the DOL starting uses VCB at switchboard that is approx 200m from motor. Now, due to lack of space in switchroom, looking to install starter more locally to motor. What are views on incorporating fuse in the local starter or just omitting it and keeping the VCB for short circuit protection.
I quite like the idea of remaining fuseless (time to replace and safety) but also thought the fuse would be of some benefit in event of fault (less stress, arc damage in situ). Possibly an unnecessary cost though. There is no existing diff protection.
Control cables need to be run between the two locations regardless of which way we go.
Would it be simplist solution for VCB to clear the overload faults as well? Or leave that locally to contactor?
(Still wondering if it is feasible to replace the VCB with fused softstarter but waiting for switchboard OEM to advise on that), that could be another topic in itself though. Think it is a non-starter (excuse the pun!) due to space though.
Thanks as always.