electrical429
Electrical
- Nov 13, 2019
- 51
As per IEEE Std C57.32 section 6.4.2 extract below Earthing Transformer continuous rating must be 3% of 10s thermal rated current.
We will be installing ZNyn11 Auxiliary Earthing transformer for the purposes of limiting 132/33 kV YNd11 power transformer 33 kV side earth fault current to 1000 A and providing site LVAC supplies. Aux. ETx will be rated at 1000A for 10s. Site LVAC load is quite small, ~200 kVA. If you go by IEEE Std C57.32 we would require Aux. Tx thermal rating of:
Instr = 1000 A for 10s
Instr per phase = 1000A / 3 = 333 A
Snstr = 3 x 33000 V/sqrt(3) x 333 A = 19.033 MVA
Based on IEEE Std C57.32 continuous rating of transformer should be 3% x 19033 kVA = 517 kVA
What happens if install 200 kVA Aux. Tx rated at 1000 A for 10s? I've seen designs where 200 and 300 kVA Aux. Earthing transformers were rated at 1000A for 10s.
We will be installing ZNyn11 Auxiliary Earthing transformer for the purposes of limiting 132/33 kV YNd11 power transformer 33 kV side earth fault current to 1000 A and providing site LVAC supplies. Aux. ETx will be rated at 1000A for 10s. Site LVAC load is quite small, ~200 kVA. If you go by IEEE Std C57.32 we would require Aux. Tx thermal rating of:
Instr = 1000 A for 10s
Instr per phase = 1000A / 3 = 333 A
Snstr = 3 x 33000 V/sqrt(3) x 333 A = 19.033 MVA
Based on IEEE Std C57.32 continuous rating of transformer should be 3% x 19033 kVA = 517 kVA
What happens if install 200 kVA Aux. Tx rated at 1000 A for 10s? I've seen designs where 200 and 300 kVA Aux. Earthing transformers were rated at 1000A for 10s.