RRaghunath
Electrical
- Aug 19, 2002
- 1,729
I am going through the drawings of a 55MW power plant. The plant is a very old one and is due for relocation in an Indian site from its original location in France. The plant has strange (un-familiar, ofcourse interesting to me for the same reason)) configuration.
The generating unit has a 50MW main generator and a 5MW, 3kV auxiliary generator on the same shaft.
The auxiliary generator is like the unit auxiliay transformer connected generator terminals that engineers of my generation are familiar with and feeds to a 3kV auxiliary power supplies switchboard.
Further, the generator neutral is isolated from ground and there is no earth fault protection in the 3kV system (there may be open delta connected residual voltage sensing relay in the VT secondary cicuit, I am yet to check-up).
I would like to hear from any one who has worked in such a power plant and learn from their experiences. Presently the prospect of uncleared earth faults in the 3kV isolated system and arcing grounds / flashovers is scaring me.
The generating unit has a 50MW main generator and a 5MW, 3kV auxiliary generator on the same shaft.
The auxiliary generator is like the unit auxiliay transformer connected generator terminals that engineers of my generation are familiar with and feeds to a 3kV auxiliary power supplies switchboard.
Further, the generator neutral is isolated from ground and there is no earth fault protection in the 3kV system (there may be open delta connected residual voltage sensing relay in the VT secondary cicuit, I am yet to check-up).
I would like to hear from any one who has worked in such a power plant and learn from their experiences. Presently the prospect of uncleared earth faults in the 3kV isolated system and arcing grounds / flashovers is scaring me.