The delta primary connection is preferred for the reason stated by bartos. However, this is not always possible if the transformer must phase out with another startup or reserve transformer connected to another source. You must determine the necessary phase shift for the auxiliary transformer in order to confirm which connection to use. If a wye primary - wye secondary connection is required for phasing, the primary neutral usually should be ungrounded to provide primary to secondary zero sequence isolation. Depending on the transformer design and the secondary grounding, the wye-wye arrangement may also require a delta-connected tertiary winding for neutral stabilization.