I am designing a approx. 20000 sq. ft. building that will be served by 8 roof top units (RTUs) in ASHRAE climate Zone 6. The RTUs have not been selected yet.
Let us look at one RTU. This typical roof top unit might serve 4 closed offices, and 2 boardrooms.
In the shoulder seasons (Spring and Fall, we want to use electrical baseboard heating as the first stage of heating (minimal amount of baseboard will be installed) to prevent overheating the office spaces not calling for heat. We would like the RTU to fire up (gas-fired) its first stage of heating only if the room temperature in 4 out of the 6 rooms is not warm enough after 10 minutes of electrical baseboard heating ouput in those rooms.
Then if room temperature in 4 out of 6 rooms is not satisfied within an additional 10 minutes, the second stage of heating at the RTU would kick in.
My question is the following: is there technologies that can accomodate such control sequence and duel heating mode? Do you have experience with such an arrangement? We want to minimize cost of the Controls and are not willing to go with a full blown BAS. As such there is no need for a centralized user interface that would tie-in data from all 8 RTUs.
I have seen some applications for Variable Volume Temperature (VVT) applications. But our applications is a Constant Volume application so I am not sure if this could work.
The way I see it is that you have one subcontroller per room that receives one temperature sensor input from the room and sends a signal output to energize a relay that powers the electrical baseboard (if temperature remains below setpoint for 5 minutes). This subcontroller also sends a temperature sensor reading and a relay state to a Controller. This controller takes readings and electric baseboard relay statuses from all rooms before making a decision to call for heat or not. This controller has therefore averaging capability and might even be able to prioritize certain rooms over others. This controller would process all input from the subcontroller located in each respective room. Then the controller would either de-energize the electrical baseboard or not (it would be nice to have this option) and call for heat at the RTU.
For cooling, a simpler scheme would be required although the need for a voting system remains.
Hopefully this is clear (enough).
Thank you
davster01
Let us look at one RTU. This typical roof top unit might serve 4 closed offices, and 2 boardrooms.
In the shoulder seasons (Spring and Fall, we want to use electrical baseboard heating as the first stage of heating (minimal amount of baseboard will be installed) to prevent overheating the office spaces not calling for heat. We would like the RTU to fire up (gas-fired) its first stage of heating only if the room temperature in 4 out of the 6 rooms is not warm enough after 10 minutes of electrical baseboard heating ouput in those rooms.
Then if room temperature in 4 out of 6 rooms is not satisfied within an additional 10 minutes, the second stage of heating at the RTU would kick in.
My question is the following: is there technologies that can accomodate such control sequence and duel heating mode? Do you have experience with such an arrangement? We want to minimize cost of the Controls and are not willing to go with a full blown BAS. As such there is no need for a centralized user interface that would tie-in data from all 8 RTUs.
I have seen some applications for Variable Volume Temperature (VVT) applications. But our applications is a Constant Volume application so I am not sure if this could work.
The way I see it is that you have one subcontroller per room that receives one temperature sensor input from the room and sends a signal output to energize a relay that powers the electrical baseboard (if temperature remains below setpoint for 5 minutes). This subcontroller also sends a temperature sensor reading and a relay state to a Controller. This controller takes readings and electric baseboard relay statuses from all rooms before making a decision to call for heat or not. This controller has therefore averaging capability and might even be able to prioritize certain rooms over others. This controller would process all input from the subcontroller located in each respective room. Then the controller would either de-energize the electrical baseboard or not (it would be nice to have this option) and call for heat at the RTU.
For cooling, a simpler scheme would be required although the need for a voting system remains.
Hopefully this is clear (enough).
Thank you
davster01