Rabbit12
Structural
- Jul 23, 2014
- 477
I've got an issue. It's completely my screw up. I specified a B-L1a WP from Table 8-2 in AISC 360. However, my plate thicknesses are 5/8" which exceed the maximum base metal thickness.
This was discovered by the weld inspector in the field. We could easily change to a B-U4a and bevel the plates but this would be field work and owner is saying they will back charge us. We can't use B-L1b because we don't meet the root opening requirements.
However, section 5.22.4.3 in AWS D1.1 says we can correct that by welding to the sides of plate at the opening to reduce the root opening to the tolerances of B-L1b? Can someone confirm that I am interpreting that section correctly?
Also, I had someone mention we could but WP. I'd never heard of that. My impression was that WP were tested to verify adequacy. Changing any parameter would void the test results.
This was discovered by the weld inspector in the field. We could easily change to a B-U4a and bevel the plates but this would be field work and owner is saying they will back charge us. We can't use B-L1b because we don't meet the root opening requirements.
However, section 5.22.4.3 in AWS D1.1 says we can correct that by welding to the sides of plate at the opening to reduce the root opening to the tolerances of B-L1b? Can someone confirm that I am interpreting that section correctly?
Also, I had someone mention we could but WP. I'd never heard of that. My impression was that WP were tested to verify adequacy. Changing any parameter would void the test results.