AWWA C207 Flange Bolting

Status
Not open for further replies.

pipe15

Mechanical
Jul 22, 2005
69
0
0
US
Does anybody know when the AWWA C207 standard changed the bolting requirement from only mentioning A307 bolting to A307 bolting for Class B & D and A-193 bolting for Class E & F.

also, AWWA C207-01 lists only A194 nuts regardless of the bolt material in lieu of what can be found in the A307 designation (A563 nuts)

any thoughts on why A-194 nuts would be required for the A307 bolting?

thanks
mark
 
Replies continue below

Recommended for you

A-194 nuts are not required in C307 bolting for Class B&D flanges per AWWA C207-07 (I suspect a clarification appeared in later standards than what you are looking at).
 
Thanks Rconner. I was looking at the 2001 edition. this is good to know since 2-3/4" nuts were already bought to the 563 standard.
 