Bronzeado
Electrical
- Jan 6, 2008
- 272
For electrical people and transformer experts in this forum,
In general, the complete B-H curve (based on the V-I curve) of large power transformers (above 100MVA) can not measured in manufacture laboratories. This is because of these labs has not anought short-circuit power to saturate deeply large transformers.
Normally, the V-I (B-H) curve is measured in a winding assembled on the ferromagnetic core by supplying voltage up to 120% of the transformer nominal voltage. After that, it is measured the V-I (B-H) curve in the same winding without the ferromagnetic core (air core reactance) and then these two curves are joined graphically.
My questions are:
1) At which point these two curves should be joined?
2) Could that point be considered as the "knee point" of the B-H curve?
These questions heve been posted to magnetic people as well.
Best regards,
Herivelto Bronzeado
In general, the complete B-H curve (based on the V-I curve) of large power transformers (above 100MVA) can not measured in manufacture laboratories. This is because of these labs has not anought short-circuit power to saturate deeply large transformers.
Normally, the V-I (B-H) curve is measured in a winding assembled on the ferromagnetic core by supplying voltage up to 120% of the transformer nominal voltage. After that, it is measured the V-I (B-H) curve in the same winding without the ferromagnetic core (air core reactance) and then these two curves are joined graphically.
My questions are:
1) At which point these two curves should be joined?
2) Could that point be considered as the "knee point" of the B-H curve?
These questions heve been posted to magnetic people as well.
Best regards,
Herivelto Bronzeado