Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

B31.1 Hydrotesting with Blind Flanges

Status
Not open for further replies.

loilfan

Mechanical
Jan 20, 2015
122
In B31.3 345.2.3 (b) Flanged Joints it says:

"Flanged joints used to connect piping components and subassemblies that have previously been tested, and flanged joints at which a blank or blind is used to isolate equipment or other piping during a test, need not be leak tested in accordance with para. 345.1."

In B31.1 137.2.5 Treatment of Flanged Joints Containing Blanks it says:

"Flanged joints at which blanks are inserted to blank off other equipment during the test need not be tested after removal of the blank provided the requirements of para. 137.7.1 are subsequently performed"

Note that para. 137.7.1 is an Initial Service Test

B31.1 distinguishes between Blind Flanges and Blanks in 104.5.2 and 104.5.3, so the exclusion of hydrotesting with blind flanges seems intentional.

Does anyone know why B31.1 seems to not permit the user to bolt flanged spools together without re-hydrotesting unless they used blanks (and did an initial service test)?
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor