tc7
Mechanical
- Mar 17, 2003
- 387
The application I have is to replace a couple of drain lines and a blow down line that empty into an exhaust pit. In one case I have a drain line that services a steam system operating at 540psig.
This 540 drain line (happens to be 1-inch line) tees into a 4-inch blow down line which services a separate steam system that operates at 600psig. My job is to replace all the 4-inch line and the 1-inch lines from its open end at the exhaust pit back to the first upstream valve in each line.
I initially thought this would require no hydro test because B31.1(2012)paragraph 137.3.2 states,"Lines open to the atmosphere, such as vents or drains downstream of the last shutoff valve, need not be tested."
However, the 1-inch line includes a check valve whose purpose is to block any blow down from the 4-inch line from going back upstream of the 1-inch line (this large 4-inch line is called a bottom blow which means there will be large discharge of steam and water when the valve is opened). So how does this check valve enter into a decision to perform a hydro or not ? There are two situations that don't seem to be addressed by the Code:
1. if the check valves ever fails shut, then the 1-inch line can become a pressure line;
2. if the check operates properly and remains closed during blow down in the 4-inch line then there will be some build-up of back pressure that any joint down stream of the 1-inch check valve will see.
Any suggestions out there on my dilemma ? to hydro or not to hydro?
Thanks.