backfill of basement walls

Status
Not open for further replies.

turnitup

Geotechnical
May 22, 2006
5
US
I have a dilema here, In the past I have always backfilled my walls without using top restraints on the walls, and so far have neve had a problem, but I want to stress that great care was taken to monitor the wall on backfill, to make sure no bowing or cracking was hapening. Here is my dilema, Im working with a PM who was quite certain he wanted the floor on the building first, before backfill, didnt happen. Time schedule for job would not allow for us to wait on framers, etc. Walls are 8" thick and 10' tall on 20"x10" footings, backfill consisted of 36" of 1 1/2" drain rock topped with class A/B screened ballast placed and compacted in lifts of 18" to a depth of 8' total.
Again I want to stress that great care was taken on monitoring the wall on backfill, we had no movement. I would encourage feedback please.
 
Replies continue below

Recommended for you

The structure may be able to function as an "open top box" if the walls are relatively short or there are jogs in the wall. Can the walls span horizontally to the corners or as a 2 way plate. If not, then the walls should be braced.

You should be able to confirm this by calculation.
 